Thread: Clueless On Electrics

  1. #1
    Hobbit Guest

    Default Clueless On Electrics

    Gday all. at the moment i have one of those 4 point boxes like you use on building sites with its own trip switch. That runs from a power lead back to the power outlet. I run my light up to 600w my hailea air pump, my pedestal, my dehumidifier my extraction fan (haha the 600 watt one Trex). That means im now piggy backed up in one of the 4 outlets. Firstly is what im doing safe, I want a couple more outlets. I was thinking to run another extension cable in and and have 2 x 6 outlet power packs mounted on a board. is this safe. Later i want to run a dyson cool/warm fan that can use up to 2000watt in as well as a dehumidifier. I dont own the house so i cant do anything drastic.

  2. The Following User Says Thank You to Hobbit For This Useful Post:

    joker_the_smoker (18-08-17)

  3. #2

    Join Date
    Apr 2015
    Location
    A Green and pleasant land
    Posts
    16,142
    Thanks
    65,121
    Been Thanked: 66,662 Times

    Default

    It's safe as long as your not overloading the extension cable/four way socket and also not overloading the circuit the extension is plugged into.


    Sent from a green pleasant land

  4. The Following 3 Users Say Thank You to British green For This Useful Post:

    David Spaid (18-08-17), joker_the_smoker (18-08-17)

  5. #3
    Hobbit Guest

    Default

    Quote Originally Posted by British green View Post
    It's safe as long as your not overloading the extension cable/four way socket and also not overloading the circuit the extension is plugged into.


    Sent from a green pleasant land
    Cheers BG.

  6. The Following User Says Thank You to Hobbit For This Useful Post:

    British green (18-08-17)

  7. #4

    Join Date
    Apr 2015
    Location
    A Green and pleasant land
    Posts
    16,142
    Thanks
    65,121
    Been Thanked: 66,662 Times

    Default

    Remember that most extension leads aren't rated past 13 amps and you can work out amps by using ohms law . Which is watts divided by volts


    Sent from a green pleasant land

  8. The Following User Says Thank You to British green For This Useful Post:

    joker_the_smoker (18-08-17)

  9. #5
    Hobbit Guest

    Default

    So I should work out the amps of all my equipment and be sure that the leads are rated for the job?

  10. The Following User Says Thank You to Hobbit For This Useful Post:

    Trex (18-08-17)

  11. #6

    Join Date
    Sep 2016
    Location
    Canada
    Posts
    16,927
    Thanks
    46,855
    Been Thanked: 56,239 Times

    Default

    Ohh remember Hobbit , on equipement start up such as pumps ,lights etc , it will make amps spike 30%

    600w is approx 6amps

    My organic diary
    https://www.thctalk.com/cannabis-foru...d.php?t=158556

  12. The Following User Says Thank You to Trex For This Useful Post:


  13. #7

    Join Date
    Aug 2017
    Posts
    316
    Thanks
    418
    Been Thanked: 973 Times

    Default

    Your cords are all fine. The question is if your amp demand is larger than breaker supplying your 4 point box, I'm not sure what a four point box is. You total amp demand is you total watts devided by you voltage. So you can run your 600w fan and 600v light on 120v supply and it will ask for 10 ampsjuat for those 2. If you run 240v than 5 amps. So you could run that one more thing like an air pump or something below 5 amps. A normal cut here in Canada is 15 amps. I am an electrician here in canada

  14. The Following 2 Users Say Thank You to David Spaid For This Useful Post:

    Trex (18-08-17)

  15. #8

    Join Date
    Sep 2016
    Location
    Canada
    Posts
    16,927
    Thanks
    46,855
    Been Thanked: 56,239 Times

    Default

    Quote Originally Posted by David Spaid View Post
    Your cords are all fine. The question is if your amp demand is larger than breaker supplying your 4 point box, I'm not sure what a four point box is. You total amp demand is you total watts devided by you voltage. So you can 600w fan and 600v light on 120v supply will ask for 10 amps. So you could run that one more thing like an air pump or something below 5 amps. A normal cut here in Canada is 15 amps. I am an electrician here in canada
    Holy fuck a Canuck , i think me and you are the only ones man

    My organic diary
    https://www.thctalk.com/cannabis-foru...d.php?t=158556

  16. The Following User Says Thank You to Trex For This Useful Post:

    David Spaid (18-08-17)

  17. #9
    Hobbit Guest

    Default

    Quote Originally Posted by David Spaid View Post
    Your cords are all fine. The question is if your amp demand is larger than breaker supplying your 4 point box, I'm not sure what a four point box is. You total amp demand is you total watts devided by you voltage. So you can run your 600w fan and 600v light on 120v supply and it will ask for 10 ampsjuat for those 2. If you run 240v than 5 amps. So you could run that one more thing like an air pump or something below 5 amps. A normal cut here in Canada is 15 amps. I am an electrician here in canada
    Cheers mate , we run on 240 here. the box is just a box with 4 outlets.

  18. The Following 2 Users Say Thank You to Hobbit For This Useful Post:

    British green (18-08-17), Trex (18-08-17)

  19. #10
    Hobbit Guest

    Default

    Quote Originally Posted by Trex View Post
    Ohh remember Hobbit , on equipement start up such as pumps ,lights etc , it will make amps spike 30%

    600w is approx 6amps

    Nice one mate.

    My organic diary
    https://www.thctalk.com/cannabis-foru...d.php?t=158556
    Quote Originally Posted by Trex View Post
    Holy fuck a Canuck , i think me and you are the only ones man

    My organic diary
    https://www.thctalk.com/cannabis-foru...d.php?t=158556
    Haha all the Aussies get banned quik smart lol.

  20. The Following User Says Thank You to Hobbit For This Useful Post:

    Trex (18-08-17)

Page 1 of 2 1 2 LastLast

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


THCtalk.com Disclaimer - You must be over 18 years old to view/use this site .THCtalk.com does not encourage growing Cannabis or possessing Cannabis. Learning how to grow Cannabis instructions should be for educational purposes only. All Information contained in this web site is for: Historical reference, Scientific reference and Educational purposes only. Visitors to this website are advised against breaking the law as It is illegal to smoke, grow, or possess cannabis in the UK and some US States